Beam for loft/hoist: Is there a legit engineer in the house?

Discussion in 'The Hokey Ass Message Board' started by Kevin Lee, Jan 4, 2012.

  1. Kevin Lee
    Joined: Nov 12, 2001
    Posts: 7,584

    Kevin Lee
    Super Moderator
    Staff Member

    Task one: Span 14' in my garage to build a loft that will be roughly 8' deep. I have access to a beam that is 6" tall, 4" wide with 1/4" thick web all around. Am I safe here? It sure LOOKS legit but I want to be sure.

    Bonus bit: I actually have access to a couple of these beams so providing it is strong enough I am considering building a gantry crane with the other.

    Thoughts from anyone here? Not storing engines in the loft – a rear end might be the heaviest thing it will support.
     
  2. That will do the job.......
    no ,I'm not an engineer but I've played one on occasion....
     
  3. Pat Pryor
    Joined: May 28, 2007
    Posts: 1,911

    Pat Pryor
    Member

    what it takes an engineer 6 months to figure out it takes 2 good men 6 hours to fix.:rolleyes:
     
  4. choppedtudor
    Joined: Nov 28, 2009
    Posts: 722

    choppedtudor
    Member

    remember, what supports the beam is as important as the beam itself....steel posts buried in the walls work out best....wood posts tend to do funny things with not-so funny results.
     

  5. 201
    Joined: Dec 17, 2002
    Posts: 344

    201
    Member

  6. Pat Pryor
    Joined: May 28, 2007
    Posts: 1,911

    Pat Pryor
    Member

    wood or steel pillers ?

    we had one about the same size and length at work and we wouldnt put over 2000 pounds on it. it may of been 3/8 thick
     
    Last edited: Jan 4, 2012
  7. general gow
    Joined: Feb 5, 2003
    Posts: 6,410

    general gow
    MODERATOR
    Staff Member

    is mr. sweet in the house?
     
  8. flatford39
    Joined: Dec 3, 2006
    Posts: 2,799

    flatford39
    Member

    Don't have my books here at home but I would be alot happier if it was an 8" or better yet a 10" WF Beam. Are you considereing a center post??? I have concerns about it sagging. As others have said it is very important as to how you support the ends and in this case possibly the center. When I am at work tomorrow I will check my steel books for capacity.
     
  9. Kevin Lee
    Joined: Nov 12, 2001
    Posts: 7,584

    Kevin Lee
    Super Moderator
    Staff Member

    I have a text in to Mr. Sweet... unanswered so far and i am impatient. :)

    The uprights are – I think – 3.5" round tubing with a plate at each end. They may be 4". One drilled to match the beam and one for a floor mount. This is being salvaged from an existing loft in a building downtown so I'm pretty confident in the deal... just looking for validation.

    Not sure how thick my slab is so I may saw holes and pour my own footers.
     
  10. Jay will know for sure, you need his number?

    I am envious, I have had plans of doing one of these since I built our place.
     
  11. Lucky3
    Joined: Dec 9, 2009
    Posts: 652

    Lucky3
    Member

    I am an engineer and you haven't provided enuff info to calculate bending loads or support loads but a 6" beam (I beam ??) is a minimal structural component for the length you mention. Both of them welded together would be a better structural member. Your deck load above the beam will be the bigger load to minimize if you want to hoist stuff (engines, etc.) A safer bet is to put a support beam in the middle that can be removed if you want the open storage area. :D
     
  12. tlmartin84
    Joined: Jul 28, 2011
    Posts: 1,030

    tlmartin84
    Member
    from WV

    That beam assuming it is a W6x12 (based on it having 1/4" flange) will carry an 8.3kips (8300 lbs) at L/360. Thats 754 lbs per 4'(half width of loft) or 188psf, which is well beyond the 60 (20 dead load and 40 Live Load) psf used in most buildings).
     
  13. Kevin try this: Support both ends on some concrete blocks, then stand in the middle, how much does it bend? That's the most direct way to see if it will support you. That's a point loading. How many other rafters will you have? What's the spacing, size, etc. All those things go into a floor loading equation. But you'll have a pretty good idea by standing on it.
     
  14. flatford39
    Joined: Dec 3, 2006
    Posts: 2,799

    flatford39
    Member

    I was thinking the same thing about welding two together but like you said not enuff info here to be sure. I suspect he has a wide flange by the dimensions and not an I beam as well.
     
  15. tlmartin84
    Joined: Jul 28, 2011
    Posts: 1,030

    tlmartin84
    Member
    from WV

    Civil engineer, and just pulled that from the AISC steel construction manual. Good to go man.
     
  16. jcapps
    Joined: Dec 30, 2008
    Posts: 473

    jcapps
    Member
    from SoCal

    a 4" x 6" steel i beam should be fine
     
  17. tlmartin84
    Joined: Jul 28, 2011
    Posts: 1,030

    tlmartin84
    Member
    from WV

    3.5" diameter with a .318" wall thickness column supports 67k's at 10' in height. So your columns are good to go to, actually treated 4x4's would work for the ends in the building as they will hold roughly 5k's.
     
  18. tlmartin84
    Joined: Jul 28, 2011
    Posts: 1,030

    tlmartin84
    Member
    from WV

    8.3Kips for uniformly distributed load. For loft.

    4Kips for Point Load. Gantry
     
  19. Why has no one made mention of "webbing" this I-beam for higher structural value .... are we not hotrodders??? LOL
     
  20. 1ton
    Joined: Dec 3, 2010
    Posts: 690

    1ton
    Member

    As a rigger/millwright I always have a load chart in my wallet. It says that a standard I beam, 6" tall @ 12.5 lbs/ft. with a 1/4" web can safely carry 1870 lbs. in the center of a 14' span. If you were to step up to an 8" beam with a 5/16" web, your capacity increases to 5330 lbs. at the center of a 14' span. 10" beam with 5/16" web is 11070 lbs. in the center at that span. I would go with an 8" or better because you know damn well that your going to store heavy stuff up there and hoist off it as well.
     
  21. Kev, why don't ya just =TRUSS= the beam with 2" square tube mirroring the dimension of your rafters?[recommend adding a vertical support from top of beam to center/peak of truss...]
    this should easily perform your tasks and really not interfere with the "loading area" of your loft..........
     
  22. VoodooTwin
    Joined: Jul 13, 2011
    Posts: 3,453

    VoodooTwin
    Member
    from Noo Yawk

    Assuming the beam isn't damaged or heavily pitted, etc. for an 8-foot deep area, you are good to go. If you plan to attach a hoist to the lower flange though, you might consider upsizing, or reinforcing it with a structural T or C-channel. Yes, I'm a registered Professional Engineer (mechanical).
     
  23. alchemy
    Joined: Sep 27, 2002
    Posts: 20,524

    alchemy
    Member

    If you drill the I-beam to lighten it, you probably won't need as heavy a post to hold it up, or thicker footings. ;)
     
  24. Mr48chev
    Joined: Dec 28, 2007
    Posts: 33,984

    Mr48chev
    ALLIANCE MEMBER

    That would cost him some of the strength and he isn't really worried about the weight of the beam on the posts as that is negligible in this case but the load capacity for the beam when it holds the loft with the 14 ft span. We build lofts in our garage and pretty soon we figure out how to start loading heavy crap up there one cylinder head or box of old hot rod magazines at a time.
     
  25. Pour footers for sure. If no one gives you numbers I have a table in one of my structural books here. I can dig it out.

    You are not going to have 14 teenagers up ther dancing right? If it is storage and not living space that effects the loading.
     
  26. phat rat
    Joined: Mar 18, 2001
    Posts: 4,922

    phat rat
    Member

    I think he was tongue in cheek with that comment
     
  27. Kevin Lee
    Joined: Nov 12, 2001
    Posts: 7,584

    Kevin Lee
    Super Moderator
    Staff Member

    Dammit... I already drilled it. Do you think I can just tack weld the slugs back in and give the whole thing a skim coat of filler?
     
  28. alchemy
    Joined: Sep 27, 2002
    Posts: 20,524

    alchemy
    Member


    Use Duraglass, it's stonger than Bondo.
     
  29. Bruce Lancaster
    Joined: Oct 9, 2001
    Posts: 21,681

    Bruce Lancaster
    Member Emeritus

    To heavily paraphrase Mart from England..."at some point you have to be willing to trust your own worthless striped wild-ass guess at structural adequacy"...

    I have on occasion in my life of poverty and desperate improvisation used some pretty scary and flimsy stuff to hold the far end of the chain hoist off of the ground...remember that if you are only heavily loading the thing while hoisting an engine, it is easy and cheap to stick in a couple of simple and temporary diagonal braces from ground to near the center of beam to add support near point of load. They can be knocked down and tossed in a corner once the engine is in, and then quickly put back twenty minutes later when you realize your throwout bearing is still on the workbench.
    I would re-worry this differently...sounds like loft is partial, and being considered for light stuff.
    My thought is that a car AT LEAST doubles in volume as it is taken apart, and I would want as much capacity up there as possible...full area, heavy plywood, add in extra wall studs and beams, use lots of screws. You want to be able to stash most of a car and be able to bring pieces up and down easily.
    I heavily reinforced and floored by loft/attic area for this so I can stash almost anything up there, and went heavy-duty on stairs so that two people carrying a shortblock could get up there without too much fear...for the stairs I got two of the pre made notched stair sides, added stout planks, and hinged the whole mess up to with a piece of pipe run through stair sides and beams. The whole thing is dragged back up into the ceiling by a light duty rope pulley hoist.
     
  30. Bruce Lancaster
    Joined: Oct 9, 2001
    Posts: 21,681

    Bruce Lancaster
    Member Emeritus

    To heavily paraphrase Mart from England..."at some point you have to be willing to trust your own worthless striped wild-ass guess at structural adequacy"...

    I have on occasion in my life of poverty and desperate improvisation used some pretty scary and flimsy stuff to hold the far end of the chain hoist off of the ground...remember that if you are only heavily loading the thing while hoisting an engine, it is easy and cheap to stick in a couple of simple and temporary diagonal braces from ground to near the center of beam to add support near point of load. They can be knocked down and tossed in a corner once the engine is in, and then quickly put back twenty minutes later when you realize your throwout bearing is still on the workbench.
    I would re-worry this differently...sounds like loft is partial, and being considered for light stuff.
    My thought is that a car AT LEAST doubles in volume as it is taken apart, and I would want as much capacity up there as possible...full area, heavy plywood, add in extra wall studs and beams, use lots of screws. You want to be able to stash most of a car and be able to bring pieces up and down easily.
    I heavily reinforced and floored by loft/attic area for this so I can stash almost anything up there, and went heavy-duty on stairs so that two people carrying a shortblock could get up there without too much fear...for the stairs I got two of the pre made notched stair sides, added stout planks, and hinged the whole mess up to with a piece of pipe run through stair sides and beams. The whole thing is dragged back up into the ceiling by a light duty rope pulley hoist.
     