    7F50C541-9DF6-4505-9045-48CAB0596573.jpeg FE451AF4-BBD2-49D9-AB9A-885F619E491F.jpeg Was doing some updating on our vintage travel trailer last night and was using several power tools on an extension cord. Obviously not at the same time. Closed up shop and went in for dinner. Came back out after church today to pick up tools and clean up a bit. Went to plug in the shop vac and no power.

    This is what I found. I have about 6-8 outlets on this run. It’s a 20A breaker.
    This is about midway in the run. Let oks like it started on the neutral side of the plug.
    Could have been a lot worse.
     
  2. I would assume your 20 amp breaker in the service Pannel saved the day by doing it's job.
     
    mad mikey and Roothawg like this.
  3. Roothawg
    Joined: Mar 14, 2001
    Posts: 25,142

    Roothawg
    Member

    Negative. It never tripped.

    I got in touch with my nephew that is working for a local electric contractor and he asked what the rating was on my outlet. It was 15 amp. I think I am going to change the breaker to a 15Amp. Never really thought much about it.

    Now I am paranoid.
     
  4. BJR
    Joined: Mar 11, 2005
    Posts: 10,471

    BJR
    Member

    Glad to hear you are not reporting on your shop fire. You dodged a bullet there. Why not change all your outlets to 20 amp outlets. A screw must have been loose to create that much heat and not trip a breaker. What was plugged into the outlet that burned?
     
  5. Budget36
    Joined: Nov 29, 2014
    Posts: 14,348

    Budget36
    Member

    Wall plugs should be on a 20 amp circuit, also the 20 amp plugs should have another “slot” in one side sticking out. That indicates a 20 amp plug. Check the wiring for the gauge and length of run.
    What’s odd is that with that much cooked, the breaker didn’t trip.
    FWIW, I don’t think a 20 amp socket is built to take more current than a 15 amp socket. I think it’s just an indicator with the slot.
    But I didn’t take many classes on residential electric.
    Maybe @Crazy Steve can shed some light.

    Edit: Also take a look at the male end of your extension cord. Clean it up with a small wire brush. As they age they corrode a bit adding resistance.
     
  6. Dang.
    I’ve got GFCI ones on every circuit. Local code.
    I also started just cutting off the main power when I’m not in it.
     
  7. rockable
    Joined: Dec 21, 2009
    Posts: 4,673

    rockable
    ALLIANCE MEMBER

    Whew! I had a near miss with the horn button sticking on my 49 Buick. It scared the crap out of me. The circuit isn't fused because GM didn't fuse it. Well, old horn buttons can short easily, so now mine is disabled and fused. Glad everything is ok. Put the right circuit breaker in there!
     
  8. Depends on what size wire is in your shop. If it's 14-2, that's 15 amp, if it's 12-2 you're good for 20 amp. Running a 20 amp breaker with a 14 gauge wire can effectively turn your wire into a heating element. Like BJR said, it looks like your receptacle had a loose connection creating resistance. But if your breaker is a 20 amp, make sure you have 12 gauge wire.
     
    Last edited: Apr 16, 2023
  9. Roothawg
    Joined: Mar 14, 2001
    Posts: 25,142

    Roothawg
    Member

    Thanks guys. There wasn’t anything plugged into this particular outlet. It’s just midway in the run. I think I used 12 gauge when I wired the shop. I did it all myself, so if it’s wrong, it’s on me. I am thinking loose connection as well. Looks like I may get to check them all.

    I think it was me taxing the system pretty hard last night. I had an extension cord drug up into the trailer and I had lights (LED) a circular saw and a sawzall up there. I did have a small fan but I would think the draw on it is pretty low. Downstream there is a small college fridge plugged in. I have moved it somewhere else just in case. It would probably have as much as the circular saw when the compressor kicks on.
     
  10. I run about 30 calls a year at the firehouse related to outlets, and everyone of them are a loose screw on the receptacle. I don't know if it's from heat cycles on the copper related to draw on the outlet or not, but it makes you wanna kill the breaker and check all of your connections lol
     
  11. Man,this could have been much worse. HRP
     
    Roothawg, 37slantback and mad mikey like this.
  12. scrappybunch
    Joined: Nov 16, 2011
    Posts: 422

    scrappybunch
    Member
    from nj

    Resistance makes heat...
    Glad the outlet is the only thing that burnt. Your lucky!
     
    rockable, Roothawg and mad mikey like this.
  13. flynbrian48
    Joined: Mar 10, 2008
    Posts: 8,441

    flynbrian48
    Member

    Wow. I had a neutral loosen up on a recep halfway in the run in my attached garage, it made there rest of the run dead but didn't heat up. I never use anything heavy in that garage, maybe a battery charger or the shop vac, but that's scary...
     
    chryslerfan55, Roothawg and mad mikey like this.
  14. Glad it was not a catastrophe Root. Scary stuff!
     
    Roothawg and Budget36 like this.
  15. big bird
    Joined: Feb 16, 2014
    Posts: 166

    big bird
    Member

    what kind of wire? CCA? or real copper?
     
  16. Budget36
    Joined: Nov 29, 2014
    Posts: 14,348

    Budget36
    Member

    Looking at the receptacle, it had to happen some time in the past since you weren’t using it. Even a loose connection wouldn’t do that if nothing was plugged into it in my mind.
    I think the bullet you dodged was from some time ago.
     
  17. When I did my shop I was told not to Daisy Chain from plug to plug directly for connections. Wire nut the wires in the box with a pig tail going to the actual plug receptacles. I'm not sure if that's a code or opinion but that is how I did it 35 years ago. That said and your photo makes me think it might be a good idea to do some inspections. Can't hurt anything.
     
  18. Doublepumper
    Joined: Jun 26, 2016
    Posts: 1,650

    Doublepumper
    Member
    from WA-OR, USA

    ^ This. I pigtail all my receptacles and don't use them in a daisy chain type hookup. Much safer, as the buss on the receptacle isn't carrying the current load for the rest of the circuit.
     
  19. H380
    Joined: Sep 20, 2015
    Posts: 488

    H380
    Member
    from Louisiana

    Its all about the wire in the walls. 15A is 14awg white romex. 20A is 12awg yellow romex. Breaker amperage is based on the wire size. You can use 15A receptacles on 12awg wire/20A breaker. But not 20A anything on 14awg.
     
  20. Hollywood-East
    Joined: Mar 13, 2008
    Posts: 2,019

    Hollywood-East
    Member

    Excellent wake up For all of us...
    Thanx for sharing...
     
    lumpy 63 and Roothawg like this.
  21. Roothawg
    Joined: Mar 14, 2001
    Posts: 25,142

    Roothawg
    Member

    I don't think it was from a previous episode @Budget36. It is basically wired in series and I had power until today. It happened after I went into the house last night. That's the part that scares me. I did notice the circular saw was struggling, but I thought I needed to swap out the blade.

    I'm not sure I understand the whole pig tail deal. Can someone explain the advantage of doing this? Dumb it down for a novice.

    I checked the wire. It is 12 gauge.
     
  22. Jmountainjr
    Joined: Dec 29, 2006
    Posts: 1,712

    Jmountainjr
    ALLIANCE MEMBER

    I suspect either a loose screw on the receptacle or a loose wire nut connector. Assuming 12-2 wire on the 20 amp circuit, nothing that you can plug into a 15 amp receptacle should tax anything assuming it's in good working order. I would consider putting a ground fault breaker on the circuit assuming that the installation was done before they were required.
     
    chryslerfan55 and Roothawg like this.
  23. Elcohaulic
    Joined: Dec 27, 2017
    Posts: 2,213

    Elcohaulic

    I smell Federal Pacific breakers..
     
    H380, bobss396 and Roothawg like this.
  24. Ebbsspeed
    Joined: Nov 11, 2005
    Posts: 6,341

    Ebbsspeed
    ALLIANCE MEMBER

    Back in the 70's and thereabouts there were a lot of buildings wired with aluminum wiring instead of copper. That aluminum wiring was notorious for developing loose connections, and the risk of an electrical fire is them was much higher. Those homes are still out there, and if you live in one it might not hurt to see if there is aluminum wiring in your walls. If there is, maybe pop open all the outlets and switches and check the connections.

    A loose connection doesn't mean that there is enough current to trip the breaker. It just means that there is additional resistance, and when current flows through a resistance it generates heat.

    He likely had the wiring "daisy chained" through the 6-8 outlets on the breaker that he mentioned. That means the wiring is run into one terminal on the outlet and out the other to the next outlet in line, so any outlet between the breaker and the outlet being used have current flowing through them. A loose connection in any of those could result in this near disaster.
     
  25. Doublepumper
    Joined: Jun 26, 2016
    Posts: 1,650

    Doublepumper
    Member
    from WA-OR, USA

    Using wire nuts, wire the receptacle to the feeder wires using separate wires at the receptacle. The wire nuts continue the circuit through to the next receptacle, instead of the small buss/connection bar on the receptacle.
    Hope that makes sense...o_O
     
  26. Roothawg
    Joined: Mar 14, 2001
    Posts: 25,142

    Roothawg
    Member

    Ah, ok. I get it now.
     
    Pist-n-Broke likes this.
  27. rusty valley
    Joined: Oct 25, 2014
    Posts: 3,900

    rusty valley
    Member

    current running thru a wire actually vibrates, causing connections to loosen up after years of service. Aluminum much more than copper. Its odd that it went with no load on it. In 2010 my shop burned up. 3 cars, tools, parts, building all gone. I have a disk with photos I'l post here some day. Electrical fire, started in the main panel. Never tripped the main breaker, and that building was fed off a panel in another building that did not trip either.
    Good for you Root, not a disaster !
     
  28. -Brent-
    Joined: Nov 20, 2006
    Posts: 7,491

    -Brent-
    Member

    I'd freak out walking into the shop and getting hit with that distinct smell.
     
  29. Boneyard51
    Joined: Dec 10, 2017
    Posts: 6,548

    Boneyard51
    Member

    I’m with Budget 36. This problem was a while in the making. Like Lloyd said, probably from a loose screw! But the loose screw will not necessarily heat up due to resistance, it heats up due to arcing ! Loose screws become mini welders! That is where your heat came from, under load. It finally just arced enough to finally loose connection.
    Still very dangerous!




    Bones
     
    chryslerfan55, Roothawg and Budget36 like this.
  30. 52HardTop
    Joined: Jun 21, 2007
    Posts: 1,090

    52HardTop
    Member

    To help understand the idea of pig tails, splice the hots together with a 6 to 8 inch pig tail for connecting to the receptacle. Do the same with the white, neutral, conductor. The only current the receptacle should carry is the amperage created by the device plugged into the receptacle. Looking at the burned up plug tells me the feed conductors were screwed into the plug and the load conductors were also. That is a very bad practice. All the current of the circuit is flowing through the small tabs the bridge the screws of the top and bottom outlets. I would highly recommend installing an Arc Fault Circuit Interrupter type breaker. If you had that type of protection, that burn out of the receptacle would not have happened. The Arc Fault breaker would have been tripping and you may have found the issue before any trouble occurred.
     
    4ever18, ffr1222k, Boneyard51 and 4 others like this.

Share This Page

Register now to get rid of these ads!

Archive

Copyright © 1995-2021 The Jalopy Journal: Steal our stuff, we'll kick your teeth in. Terms of Service. Privacy Policy.

Atomic Industry
Forum software by XenForo™ ©2010-2014 XenForo Ltd.